Service Interrruption, Multiple Servers Affected

We appear to have a switch or circuit down, Techs are currently investigating the issue. This is affecting the TAZ, DEXTER, HUGO, XIS, EVA, SIX, ASTRO, DEEDEE, ZAT, REI and WALLE Community servers. All MQS dedicated servers are unaffected.

We will post as soon as services have been brought back up, and will post further details and updates as they come in.

Our apologies,
Mike
Mike is offline  
Old 08-29-2021, 01:10 PM   Postid: 188524
 Mike
Service Assistant
 
Mike's Avatar
 
Join Date: Jan 2011
Posts: 256
Re: Service Interrruption, Multiple Servers Affected

Attempts to restore services remotely have met with no success. Preliminary investigation suggests we lost a power source, or (hopefully) just the breaker to it. Kevin is en route to the data center now.

We will continue to report any updates as the information comes in.
Mike is offline  
Old 08-29-2021, 01:34 PM   Postid: 188525
 Mike
Service Assistant
 
Mike's Avatar
 
Join Date: Jan 2011
Posts: 256
Re: Service Interrruption, Multiple Servers Affected

Kevin arrived shortly ago and services to the affected community servers are coming back up now. The issue is that the breaker on a power controller had failed.

Event Start: 12:42 PM EST
Event End: 1:31 PM EST

Duration: 49 minutes

Last edited by Mike : 08-29-2021 at 01:34 PM. Reason: typo
Mike is offline  
Old 08-29-2021, 03:25 PM   Postid: 188526
 Kevin
Systems Administrator
 
Kevin's Avatar
 
Join Date: Aug 2001
Location: Orlando, FL
Posts: 2,986
Re: Service Interrruption, Multiple Servers Affected

If anyone is curious this was the current version of the power controller:
https://www.apc.com/shop/us/en/produ...ckets/P-AP8932
It has 2 breakers that control the top and bottom halves. The one for the top half had tripped. We have 3 of those particular models of power controller and this happened to us once before but on a different one.

Essentially, we have no reason to believe this was anything but a fluke on an otherwise reliable piece of infrastructure.
__________________
Kevin
Kevin is offline  


Currently Active Users Viewing This Thread: 1 (0 members and 1 visitors)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 12:23 AM.


Running on vBulletin®
Copyright © 2000 - 2019, Jelsoft Enterprises Ltd.
Hosted & Administrated by FutureQuest, Inc.
Images & content copyright © 1998-2019 FutureQuest, Inc.
FutureQuest, Inc.